Question Regarding Conduit Fill. | Mike Holt's Forum
Maybe your like
Menu
- Home
- Forums New posts Search forums
- What's new New posts
Search
Everywhere Threads This forum This thread Search titles only Search Advanced search…- New posts
- Search forums
- Home
- Forums
- Active Forums
- Electrical Calculations / Engineering
- Thread starter rickcola813
- Start date Oct 26, 2020
rickcola813
Member
Location New York City Occupation Project Manager I built a simple spreadsheet to help me assess conduit fill. I just ran into a conflict with an engineer. They are asking for us to pull 3 @ #2 AWG THHN conductors into 1" EMT. My spreadsheet shows that 3 @ #2AWG THHN conductors have a combined CMA of .3472 cubic inches. The spreadsheet also shows that the cross sectional area of 1" EMT is .864". When .3472 is divided into .864 I get 40.2%; which is greater than the 40% required. Am I calculating incorrectly or is it acceptable to round the answer up or down to the nearest number therefore making 40.2% acceptable?infinity
Moderator
Staff member Location New Jersey Occupation Journeyman Electrician (retired) According to Table C1: 1" EMT is large enough for 3-#2 THHN conductors. Although not an official part of the NEC the tables are fairy accurate for use when sizing raceways. Welcome to the Forum.dkidd
Senior Member
Location here Occupation PErickcola813 said: I built a simple spreadsheet to help me assess conduit fill. I just ran into a conflict with an engineer. They are asking for us to pull 3 @ #2 AWG THHN conductors into 1" EMT. My spreadsheet shows that 3 @ #2AWG THHN conductors have a combined CMA of .3472 cubic inches. The spreadsheet also shows that the cross sectional area of 1" EMT is .864". When .3472 is divided into .864 I get 40.2%; which is greater than the 40% required. Am I calculating incorrectly or is it acceptable to round the answer up or down to the nearest number therefore making 40.2% acceptable? Click to expand...Notes to Tables (7) When calculating the maximum number of conductors or cables permitted in a conduit or tubing, all of the same size (total cross-sectional area including insulation), the next higher whole number shall be used to determine the maximum number of conductors permitted when the calculation results in a decimal greater than or equal to 0.8. When calculating the size for conduit or tubing permitted for a single conductor, one conductor shall be permitted when the calculation results in a decimal greater than or equal to 0.8.
LarryFine
Master Electrician Electric Contractor Richmond VA
Location Henrico County, VA Occupation Electrical Contractorinfinity said: According to Table C1: 1" EMT is large enough for 3-#2 THHN conductors. Click to expand...Here, too: http://www.electrician2.com/rveltrain05/rf_calculator.html R
Rock86
Senior Member
Location new york Occupation Electrical Engineer / Electrician Looking at Annex C, it says 1" EMT. But if you use the information provided in Chapter 9, 1" EMT @40% is 0.346 in^2. (3) #2 THHN conductors is technically just over that number. Would the AHJ refer you to Ch.9 or Annex C?don_resqcapt19
Moderator
Staff member Location Illinois Occupation retired electricianRock86 said: Looking at Annex C, it says 1" EMT. But if you use the information provided in Chapter 9, 1" EMT @40% is 0.346 in^2. (3) #2 THHN conductors is technically just over that number. Would the AHJ refer you to Ch.9 or Annex C? Click to expand...Annex C is not enforceable code, just information. The rules in Chapter 9 apply. However the rules in Chapter 9 permit three 2AWG THHN in 1" EMT. That is a result of applying Note 7 to Table 1 in Chapter 9. That permits the next higher number of conductors of the same size when the fraction is equal to or greater than 0.8. In this case the 40% area of the raceway is 0.333 square inches and the area of the conductor is 0.1158 square inches. When you divide 0.333 by 0.1158 you get 2.87, so Note 7 lets you round up to 3. NOTE: I was not paying attention when I did this post...just looked at the first table that showed up for the area of the raceway, as that has been EMT in the past, however it is actually ENT and the area I used is not correct, however the area I used results in a good example for the round up provision of Note 7, to Chapter 9, Table 1. Last edited: Oct 27, 2020 R
rickcola813
Member
Location New York City Occupation Project Managerinfinity said: According to Table C1: 1" EMT is large enough for 3-#2 THHN conductors. Although not an official part of the NEC the tables are fairy accurate for use when sizing raceways. Welcome to the Forum.Thanks for welcoming me in Robert. While I understand there are sources such as above and references such as Ugly's and the like, It is not unusual to have different sized conductors in one conduit, hence the need for my spreadsheet. Here is my rephrased question: When I calculate the allowable number of #2AWG THHN conductors in a 1" EMT conduit, my fill percentage came to 40.2%. In my world that is above the 40% allowed. Where am I wrong here? If the fill percentage is over 40% but under 40.5% is that why it is acceptable? Is someone allowed to round to the nearest whole number?Click to expand...
LarryFine
Master Electrician Electric Contractor Richmond VA
Location Henrico County, VA Occupation Electrical Contractorrickcola813 said: It is not unusual to have different sized conductors in one conduit, hence the need for my spreadsheet. Click to expand...Check out the link I posted in post #4.
Here is my rephrased question: When I calculate the allowable number of #2AWG THHN conductors in a 1" EMT conduit, my fill percentage came to 40.2%. In my world that is above the 40% allowed. Where am I wrong here? If the fill percentage is over 40% but under 40.5% is that why it is acceptable? Is someone allowed to round to the nearest whole number? Click to expand...Because you're calculating the quantity of conductors allowed in a given size of conduit, not the size of conduit required for a given quantity of conductors (although that really is what we need to deduce). As Don pointed out in post #6, it's the quantity of permitted conductors that is allowed to be rounded up, not the size of conduit that may be rounded down.
kwired
Electron manager
Location NE Nebraska Occupation EC Field experience says if this is short run and maybe only two 90 degree bends max - maybe is ok, especially if wanting to pull through something that is already existing. Long run and/or up to allowed 360 degrees of bend - probably better to go next size on the raceway. RRock86
Senior Member
Location new york Occupation Electrical Engineer / Electricianrickcola813 said: Thanks for welcoming me in Robert. While I understand there are sources such as above and references such as Ugly's and the like, It is not unusual to have different sized conductors in one conduit, hence the need for my spreadsheet. Here is my rephrased question: When I calculate the allowable number of #2AWG THHN conductors in a 1" EMT conduit, my fill percentage came to 40.2%. In my world that is above the 40% allowed. Where am I wrong here? If the fill percentage is over 40% but under 40.5% is that why it is acceptable? Is someone allowed to round to the nearest whole number? Click to expand...Following everyone's comment I figured I'd throw up some more math... hopefully a simplified enough.. (Note: Using 2020 NEC) Table 4: 1" EMT area = 0.349in^2 Table 5: #2 THHN area = 0.1158 Notes to Tables #7: (Area of conduit) / (Area of conductor) = Number of conductors --> 0.349in^2 / 0.1158in^2 = 3.014 --> 3.014 is less than 3.800 therefore you are not allowed to round up and may have only (3) #2 THHN conductors in a 1" EMT conduit. If you wanted to know about how many #1/0 THHN you could fit --> 0.349 / 0.1855 = 1.881 --> 1.881 is greater than 1.800 therefore you are allowed to round up to (2) #1/0 THHN conductors in 1" EMT conduit.
infinity
Moderator
Staff member Location New Jersey Occupation Journeyman Electrician (retired)Rock86 said: Following everyone's comment I figured I'd throw up some more math... hopefully a simplified enough.. (Note: Using 2020 NEC) Table 4: 1" EMT area = 0.349in^2 Table 5: #2 THHN area = 0.1158 Notes to Tables #7: (Area of conduit) / (Area of conductor) = Number of conductors --> 0.349in^2 / 0.1158in^2 = 3.014 --> 3.014 is less than 3.800 therefore you are not allowed to round up and may have only (3) #2 THHN conductors in a 1" EMT conduit. If you wanted to know about how many #1/0 THHN you could fit --> 0.349 / 0.1855 = 1.881 --> 1.881 is greater than 1.800 therefore you are allowed to round up to (2) #1/0 THHN conductors in 1" EMT conduit. Click to expand...I didn't do the math but according to the table the bold part is incorrect. You're only allowed 1-#1/0 THHN in a 1" EMT, likely because the conduit fill for 2 conductors drops to 31%. R
Rock86
Senior Member
Location new york Occupation Electrical Engineer / Electricianinfinity said: I didn't do the math but according to the table the bold part is incorrect. You're only allowed 1-#1/0 THHN in a 1" EMT, likely because the conduit fill for 2 conductors drops to 31%. Click to expand...Fair point... I was showing calculations which resulted over the .8. So yes... after determining the results brings us to 2 wires, we would have to drop to 31% which would mean only (1) 1/0 THHN would be allowed. (Using 31% conditions now knowing only 2 conductors are allowed... .268/.1855 = 1.44 --> 1.44 < 1.80 = (1) 1/0 THHN)
don_resqcapt19
Moderator
Staff member Location Illinois Occupation retired electricianRock86 said: Following everyone's comment I figured I'd throw up some more math... hopefully a simplified enough.. (Note: Using 2020 NEC) Table 4: 1" EMT area = 0.349in^2 Table 5: #2 THHN area = 0.1158 Notes to Tables #7: (Area of conduit) / (Area of conductor) = Number of conductors --> 0.349in^2 / 0.1158in^2 = 3.014 --> 3.014 is less than 3.800 therefore you are not allowed to round up and may have only (3) #2 THHN conductors in a 1" EMT conduit. If you wanted to know about how many #1/0 THHN you could fit --> 0.349 / 0.1855 = 1.881 --> 1.881 is greater than 1.800 therefore you are allowed to round up to (2) #1/0 THHN conductors in 1" EMT conduit. Click to expand...After I found the correct table, it shows 0.346 for the 40% fill area for 1" EMT in my code book. That will change your numbers. 0.346/0.1158 = 2.988. Still an example of the round up rule in Note 7. Status Not open for further replies. Share: Facebook X (Twitter) Reddit Pinterest Tumblr WhatsApp Email Share Link
- Home
- Forums
- Active Forums
- Electrical Calculations / Engineering
Tag » How Many #6 Thhn In 3/4 Emt
-
Conduit Fill Table
-
Conduit Fill Table - Resources - Supply Chain Solutions
-
[PDF] Conduit Wire Fill | Western Tube
-
[PDF] NEC TABLE C CONDUCTOR SIZE – AWG / Kcmil – THHN / THWN
-
Conduit Fill Table - Electrical References - Elliott Electric Supply
-
Conduit-Fill-Table - ARROW ELECTRICAL SUPPLY
-
Q&A: 3/4-Inch Conduit Capacity - JLC Online
-
[PDF] CONDUIT FILL - Electric Supply
-
What's The Largest Gauge THHN Conductor I Can Add Three Of To An ...
-
Conduit Fill Table - Construction Monkey
-
Conduit Fill Chart - ADI Wire
-
Maximum Number Of Electrical Wires Allowed In Conduit - The Spruce
-
How To Determine Fill Limits When Using Different Gauge Wires
-
Getting Conflicting Info Regarding Conduit Fill : R/electricians - Reddit